Exposed Metal Parts Within Panels
https://brainfiller.com/arcflashforum/viewtopic.php?f=10&t=5926
Page 1 of 1

Author:  jmoore284@gmail.com [ Wed Dec 11, 2024 8:48 am ]
Post subject:  Exposed Metal Parts Within Panels

Recently I have observed multiple panelboard installations at different facilities in which the studs used to wall mount the panel are not protected. These studs extend well within the panel and conductors route against them which is not appropriate. In most instances I see red rubber caps installed over the studs to guard against this. Is this specifically called out in the NEC or in any UL standard for the construction of panels?

Attachments:
panel stud.jpg
panel stud.jpg [ 112.74 KiB | Viewed 531154 times ]

Author:  mpparent [ Thu Dec 12, 2024 8:20 am ]
Post subject:  Re: Exposed Metal Parts Within Panels

Check out NEC 312.10.

Mike

Author:  JBD [ Fri Dec 13, 2024 11:23 am ]
Post subject:  Re: Exposed Metal Parts Within Panels

The factory mounting studs are not prohibited by the equipment listing standards.
This is an installation issue, where the qualified installer should know that abrasion protection must be added as needed.