100questions wrote:
(Since we don't do proper maintenance I believe the hazard exists.)
So you can't use 70E. Chapter 2 makes it very clear that to follow 70E, you MUST perform "proper maintenance". They leave you hanging by not defining it but nevertheless, it is required. Article 130 backs this up by stating in the fine print notes that effectively, your incident energy study is utterly worthless if proper maintenance isn't being done because the breakers won't trip as expected. We do not currently have a code specifically for sites that don't do proper maintenance. When that one comes out, then that's the one you follow.
Try this little experiment to see what could happen. First, take a spreadsheet copy of your arc flash study. Ignore every incident energy that is fuse protected because those don't change (almost all fuses don't rely on mechanical motion for tripping...yes, I'm aware of SM-5's). Since incident energy is linear with time, recalculate any that are under 2 seconds up to what they would be if the breakers failed or failed to trip in a reasonable amount of time. So for instance a 4 cal/cm^2 incident energy with a 0.1 second opening time becomes 4*(2/.1) = 4*20 = 80 cal/cm^2. The reality is that this approach is somewhat overly conservative because in reality you'd have to delete/short each breaker individually and then recalculate because the chances of multiple breakers failing to trip properly is much less than a single failure, but it gives you some idea of just how really bad a system that isn't properly maintained really is in the event of an arc flash. Typically you will find that half of the previously considered "safe" cases are now well beyond available PPE.
Quote:
Let's suppose you know you have a switch you need to operate and you have been told the IE is 100cal but you have no arc flash PPE. Assume you know you can operate the switch with a rope and pulleys safely. What distance do you need to be away and or what barrier do you need between you and the switch to be able to do this in your birthday suit "in a code compliant manner."
OK by ignoring Chapter 2 and not properly maintaining it, you simply can't "get there from here". 70E makes it pretty clear that simply "suiting up" is not an acceptable alternative to practising proper maintenance. This would be akin to a particular Fortune 500 corporation whose policy is that they "don't do energized work". In other words, they follow Article 120 but flat out ignore Article 130. Interesting...I asked them whether or not they test for absence of voltage. Answer was yes, so I asked them how they test for absence of voltage which is energized work without doing energized work. In your case, you are choosing to follow Article 130 while ignoring chapter 2 and even ignoring the notes in Article 130 which specifically tell you that you can't do an incident energy study without doing proper maintenance.
That being said.
The shape of the enclosure matters. Deeper enclosures create a more "directed" radiated heat as opposed to open air conditions where it radiates equally in all directions. This is reflected by the exponent "x" which is in the equipment table in IEEE 1584 and is also listed in Annex D in 70E. This number varies from around 1.3 to 2.0 where the lower the number, the more "directed" the arc flash.
You then calculate:
new incident energy=((old distance)^x)/((new distance)^x)*old incident energy
But there is a vastly simpler approach, one that you probably already have. The "arc flash boundary" which is part of your study gives the distance at which the incident energy is less than 1.2 cal/cm^2, a point where arc flash PPE is no longer required. So stay that far away and you are in the clear. Note that the distance is calculated based on the bus bars in the back of the enclosure to a point roughly around the throat area halfway on a line between the tip of the nose and the center of the chest.
Quite often especially with transformer secondaries this will put you several feet/meters beyond the building or room. So anything that would be considered a decent fire wall is a "barrier". Remember that this is all about thermal radiation (infrared heat) so once you are out several feet/meters from the hot gases, shrapnel, etc., then anything that gets you out beyond "visible" range counts. There is a fallacy to this though...the hot gases will have a tendency to "roll" around corners of barriers especially if they are close by. Watch youtube videos of tests of arc flash blankets and you will see what I mean. Although the arc flash blankets (which are definitely a substantial barrier) more than provide enough of a barrier when sized properly, the arc flash still tends to "roll" around the corner so some arc resistant PPE is still required to protect against this. Again the manufacturers of these products have lots of design information and can help you out in this regard if the building/room itself is not an acceptable solution.