 Post subject: 2012 proposed low voltage table
PostPosted: Thu Feb 12, 2009 5:00 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
Is this the most recent version?

So please help me understand: A 2500kVA 5.3% 277/480 three phase padmount transformer is feeding a panel board. The voltage puts me in column two. Energized work at the panel requires 40 cal/cm^2 from row 3 and note 6. Work at the padmount transformer terminals, however, requires 4 cal/cm^2, from row 4 and note 1. Does this order of magnitude change in IE make sense to anyone?


Attachments:
Mouse2.jpg
Mouse2.jpg [ 22.83 KiB | Viewed 28435 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 12, 2009 6:23 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
stevenal wrote:
Is this the most recent version?

So please help me understand: A 2500kVA 5.3% 277/480 three phase padmount transformer is feeding a panel board. The voltage puts me in column two. Energized work at the panel requires 40 cal/cm^2 from row 3 and note 6. Work at the padmount transformer terminals, however, requires 4 cal/cm^2, from row 4 and note 1. Does this order of magnitude change in IE make sense to anyone?


Don't know what's up here, but our proposed tables do not match. I have attached the one that I have. Maybe someone else can shed some light on this.

Alan


Attachments:
GMIRRS.jpg
GMIRRS.jpg [ 52.76 KiB | Viewed 28436 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Feb 13, 2009 10:25 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
Do the footnotes match?
I'm guessing my version is more recent, with the inclusion of network systems.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Feb 13, 2009 10:27 am 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
Alan's version is what was presented in the recent APPA Webinar. It treats panels the same as pad-mount transformers.

Where did your's come from Stevenal?

As far as I know, these are based on limited tests done by one utility. I understand that IEEE is making additional tests. The actual table that makes it into NESC-2012 may be quite different from either of these. We are not making recommendations based on the proposed table, but are making our clients aware of it.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Feb 13, 2009 2:04 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
jghrist wrote:
Where did your's come from Stevenal?


APPA safety email list in September, prior to voting. Guess Alan's is more recent. Perhaps networks will be adressed outside of the table.

Know where I might find the footnotes or the whole *.ppt?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Feb 13, 2009 2:32 pm 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
You might be able to get it from APPA http://www.appanet.org/ . Since the Webinar was only open to APPA members or for a fee, I assume that it is copyrighted.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Oct 05, 2009 11:34 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
So I have the the proposed table which is out for comment. Any ideas on why a footnote describing 50 - 240 V testing is referenced from a cell in the 251 - 500 V column? From the last row.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883