How do you guys typically model PDUs? Do you model each component like an individual component? do you model the wiring in-between?

For example, a recent project includes an IT floor with CRACs, PDUs, and server equipment. A typical trunk might include a distribution panel feeding a number of PDUs, which comprise a 480V, 200A breaker>few feet of conductor>transformer>two "panel" main 225A breakers>misc. branch circuit breakers, including one 3-pole 100a breaker which feeds a subsequent panel 20'-150' away.

I'm inclined to model each component, however the PDU transformers have no impedance numbers on their nameplates. I know transformers of that size typically range from 2-5%, but I've also heard that PDU transformers tend to have lower impedances.

Do you guys typically model every component or treat them as a single component?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling PDUs
PostPosted: Fri Jul 31, 2026 12:47 pm 

Joined: Mon Jul 27, 2026 8:58 am
Posts: 2
Every component...

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling PDUs
PostPosted: Fri Aug 07, 2026 1:31 pm 
Sparks Level

Joined: Fri Sep 28, 2018 7:32 am
Posts: 61
Location: Sioux Falls, SD
Every component. I've not seen a PDU with isolation so you'll likely label with the worst case IE and the highest voltage.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling PDUs
PostPosted: Wed Aug 12, 2026 12:07 pm 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 67
jmoore284@gmail.com wrote:
Every component. I've not seen a PDU with isolation so you'll likely label with the worst case IE and the highest voltage.

Thanks, guys. So question: What do you consider an appropriate estimation for impedance? Despite being a well-known brand of PDU, the transformers do not list impedance. I'm hesitant to estimate for impedance because it has such an outsized effect on incident energy.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling PDUs
PostPosted: Wed Aug 12, 2026 12:14 pm 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 67
Here's an example photo of what I'm talking about.


Attachments:
File comment: Here's an example.
PDUZ.png
PDUZ.png [ 2.86 MiB | Viewed 356 times ]
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883