How to model a Fused circuit breaker in SKM
https://brainfiller.com/arcflashforum/viewtopic.php?f=23&t=5818
Author:  jsoar [ Tue Aug 13, 2024 8:13 am ]
Post subject:  How to model a Fused circuit breaker in SKM
How do I model a Fused circuit breaker in SKM? The breaker is 800A Cutler-Hammer DSL-206.
Author:  bbaumer [ Tue Aug 13, 2024 3:19 pm ]
Post subject:  Re: How to model a Fused circuit breaker in SKM
Looks like you have an Eaton Magnum DS with current limiters. Just put the breaker and current limiting fuses in series with each other. Here is an example but I don't know exactly which breaker you have or what the amp rating is of the limiter so I just somewhat randomly picked them. This is in SKM.
Author:  jsoar [ Tue Aug 13, 2024 6:47 pm ]
Man, I think I have modeled it incorrectly. I thought it was fuse then breaker.
File comment: Another example for cb 6
File comment: It's cb 6, 7, & the main circuit breaker.
Author:  bbaumer [ Tue Aug 13, 2024 11:07 pm ]
Not sure why it would make any difference. I have a customer with this type of gear and have the shop drawings with factory one-lines I can check but not until Thursday.
You might be right. I can't remember if it's breaker then fuse or fuse then breaker. Again though, makes no difference for anything downstream.
Author:  bbaumer [ Tue Aug 13, 2024 11:24 pm ]
Looks like you probably are correct fuse then breaker if I'm seeing this pic correctly.
Author:  bbaumer [ Wed Aug 14, 2024 1:32 pm ]
Bus then limiter then breaker according to some old shops I had. You were correct: