| Author |
Message |
|
jsoar
|
Post subject: Series Rating a Panelboard. Posted: Tue Aug 05, 2025 5:02 am |
|
Joined: Wed Jun 12, 2024 5:19 am Posts: 35
|
|
Hello, If I needed to series-rate a panelboard. Do I enter the rating of the breaker in the Series rating box under the component subview? I know in EasyPower I would select a check mark and it would pass on the device evaluation because it is still showing up as a fail on skm. Am I missing a step?
|
|
| Top |
|
 |
|
jsoar
|
Post subject: Re: Series Rating a Panelboard. Posted: Tue Aug 05, 2025 8:08 am |
|
Joined: Wed Jun 12, 2024 5:19 am Posts: 35
|
|
Yes, but what about the device evaluation? is there a way to show it as passed because it is being series rated?
|
|
| Top |
|
 |
|
bbaumer
|
Post subject: Re: Series Rating a Panelboard. Posted: Tue Aug 05, 2025 10:42 am |
|
| Arc Level |
 |
Joined: Fri Jul 08, 2016 10:01 am Posts: 497
|
|
Mike is correct.
If you enter a series rating in the Component Editor for the device, or bus, and that rating is higher than the X/R adjusted, calculated available fault current, it will pass the Device Evaluation.