| Series Rating a Panelboard. https://brainfiller.com/arcflashforum/viewtopic.php?f=23&t=6309 |
Page 1 of 1 |
| Author: | jsoar [ Tue Aug 05, 2025 5:02 am ] |
| Post subject: | Series Rating a Panelboard. |
Hello, If I needed to series-rate a panelboard. Do I enter the rating of the breaker in the Series rating box under the component subview? I know in EasyPower I would select a check mark and it would pass on the device evaluation because it is still showing up as a fail on skm. Am I missing a step? |
| Author: | jsoar [ Tue Aug 05, 2025 8:08 am ] |
| Post subject: | Re: Series Rating a Panelboard. |
Yes, but what about the device evaluation? is there a way to show it as passed because it is being series rated? |
| Author: | bbaumer [ Tue Aug 05, 2025 10:42 am ] |