It is currently Tue Sep 29, 2026 2:42 am
What is the largest arc flash study you have been involved with?
0 – 200 buses 20%  20%  [ 10 ]
200-500 buses 12%  12%  [ 6 ]
500-1000 buses 20%  20%  [ 10 ]
1000-2000 buses 29%  29%  [ 14 ]
More than 2000 buses – OK, how many buses? 18%  18%  [ 9 ]
Total votes : 49
 Post subject: Largest Arc Flash Study?
PostPosted: Sun Dec 06, 2020 1:53 pm
We will call this week’s question “bragging rights�
It is simple and to the point regarding the size of arc flash studies based on the number of buses.
What is the largest arc flash study you have been involved with for one facility - either performing or having a consultant performed it.
0 – 200 buses
200-500 buses
500-1000 buses
1000-2000 buses
 Post subject: Re: Largest Arc Flash Study?
PostPosted: Mon Dec 07, 2020 7:05 pm
We have worked and presently working on some very large data centers. I worked on one data center that had 2,824 buses.
PostPosted: Sun Dec 13, 2020 11:16 am
Amazing. Thanks for sharing!
PostPosted: Thu Dec 31, 2020 7:40 am
With my previous employer we created and maintained a single model (required EasyPower due to the size) exceeding 20,000 buses for a large automotive manufacturer. Hands down the best experience of my career. Many utility feeds, several generators, loads of all types, overhead bus ducts, you name it. Luckily the client wanted it to be "the most detailed analysis in North America" and had us verify every wire and necessary component down to the very last device operating at 208V or greater. No assumptions were made. Arc flash analysis, coordination, short-circuit studies, SCCR evaluations of all new equipment added to the system. Great experience!
PostPosted: Tue May 04, 2021 3:27 am
3000+ bus power plant.