I also found this file which helps some. The curves in the SKM library are showing the 104A fuse blowing at 25 amps and the 150A fuse blowing at about 50-60 amps (both long time), not 104 and 590 as the attached file suggests. The SKM curves don't even allow for transformer inrush.
Noticed this in the notes for the library file for the 9F59T:
8-83
These backup fuses are designed to interrupt currents above the minimum I/C shown below.
Fuses must be coordinated with a series device capable of clearing lower currents.
Rating (Amps) Min I/C (Amps)
40C 280
50C 300
65C 440
80C 580
100C 830
125C 475
150C 590
250C (2-125C) 900
300C (2-150C) 1080
And this for the 9F54WLD:
Current ratings are not assigned to distribution transformer internal fuses.
Refer Ermco Components Inc, for the KAIC and actual Amp ratings.
Doc # 32B548089(2 sheets)
Model Number Amp Rating (A)
9F54WLD002 24
9F54WLD102 41
9F54WLD202 74
9F54WLD302 104
9F54WLD303 104
9F54WLD402 146
9F54WLD502 200
9F54WLD602 272
File comment: More info on these fuses
Types-Ratings-of-Expulsion-Fuses-.pdf [19.8 KiB]
Downloaded 585 times