Nerf,
The complex phrasing is sometimes difficult to follow, even without the additional complexity of working in a second language. I understand your confusion!
The text at the beginning of Article 130.5(F) includes this statement:
Quote:
The results of an incident energy analysis to specify an arc flash PPE category in Table 130.7(C)(15)(c) shall not be permitted.
This is a mandatory statement, not a flexible statement. It is not permitted.
Table 130.7(C)(15)(c) is
only for use with the "Arc Flash PPE Categories method," as described in Article 130.7(C)(15). That is:
- Refer to Table 130.7(C)(15)(a) for AC systems, or Table 130.7(C)(15)(b) for DC systems, to see which PPE category applies to the task/equipment. If the task/equipment is not listed, this approach is not permitted.
- If a PPE category is found, refer to Table 130.7(C)(15)(c) to see which PPE elements are needed for that PPE category.
Some facilities have continued to use the categories as a shorthand method to
communicate to workers about what PPE is needed. The standard prohibits employers from using the categories to
decide what PPE is needed (when an incident energy analysis is performed). The distinction is problematic, even for native English speakers.