| Author |
Message |
|
Leonard
|
Post subject: Voltage Systems according to NEC Posted: Mon Jun 29, 2020 8:40 am |
|
Joined: Tue Jul 01, 2014 8:40 am Posts: 111
|
|
Hi Folks
Greetings from North of the Border. Here in Canada we basically have 3 voltage range systems according to our CEC Part 1: Extra Low Voltage- 1-30V Low Voltage - 31-750V High Voltage- greater than 750V
What would be the same under the NEC? I believe that you also refer to Medium voltage and Ultra High Voltage as well?
Thanks allot Best regards
Len
|
|
| Top |
|
 |
|
Brian_K
|
Post subject: Re: Voltage Systems according to NEC Posted: Wed Jul 15, 2020 10:35 am |
|
Joined: Wed Jul 15, 2020 10:28 am Posts: 1
|
|
Hi Len,
In the U.S. nominal voltage ratings for 60Hz electric power systems above 100V are specified by ANSI C84.1
3 System Voltage Classes 3.1 Low Voltage (LV): A class of nominal system voltages 1000 volts or less. 3.2 Medium Voltage (MV): A class of nominal system voltages greater than 1000 volts and less than 100 kV. 3.3 High Voltage (HV): A class of nominal system voltages equal to or greater than 100 kV and equal to or less than 230 kV. 3.4 Extra-High Voltage (EHV): A class of nominal system voltages greater than 230 kV but less than 1000 kV. 3.5 Ultra-High Voltage (UHV): A class of nominal system voltages equal to or greater than 1000 kV.
Aloha, Brian
|
|
| Top |
|
 |
|
Leonard
|
Post subject: Re: Voltage Systems according to NEC Posted: Mon Jul 20, 2020 7:29 pm |
|
Joined: Tue Jul 01, 2014 8:40 am Posts: 111
|
|
Hi Brian,
Excellent and thank you so much for the information
All the Best to you
Len
|
|