It is currently Sun Nov 22, 2026 10:17 am
 Post subject: Under calibrated PPE?
PostPosted: Wed Mar 01, 2023 9:51 am
Hello everyone,
I am new to the forum.
I would like to ask ,in what way is 25 cal/cm2 arc protected clothing possible to be classified 2.cat.
Thanks for your help
Tibor
 Post subject: Re: Under calibrated PPE?
PostPosted: Mon Mar 06, 2023 10:51 am
70E Table 130.7(C)15(c) Personal Protective Equipment is the table used for the PPE Categories method. In that Table PPE 1 goes to 4 cals, PPE 2 goes to 8 cals, PPE 3 - 25 cals and PPE 4 - 40 cals.
Category 2 is good for 8 calories, but anything larger can be used for a lower incident energy rating, so a 25-cal PPE can be used for Cat 2.
PostPosted: Mon Mar 06, 2023 12:39 pm
Thank you for your reply,
So, a cloth is marked with 25 cal/cm and 2 CAT.
Which one is relevant?
PostPosted: Thu Mar 09, 2023 12:58 am
mpparent wrote:
Might be helpful to take a picture of the tag and post it here.
File comment: There is an explanation
PostPosted: Fri Mar 10, 2023 12:45 am
mpparent wrote:
Does the garment have a tag on the inside, indicating its ATPV?
Yes,
ATPV25 cal/cm2
IEC61482 1-2
NFPA 70
PostPosted: Fri Mar 10, 2023 1:15 am
Tboy01 wrote:
Yes,
ATPV25 cal/cm2
IEC61482 1-2
NFPA 70
The class 2 refers to APC 2 (Arc Protection Class 2) according to IEC61482-1-2 (european Box Test) and is independent from the ATPV value
PostPosted: Fri Mar 10, 2023 2:33 am
MarkusK wrote:
Tboy01 wrote:
Yes,
ATPV25 cal/cm2
IEC61482 1-2
NFPA 70
Yes, it's clear.
I needed confirmation that I did indeed need to replace the protective clothing.
Thank you for the time you have spent on this topic
Sincerely
Tibor
