It is currently Fri Sep 25, 2026 1:02 am
 Post subject: Series Rating a Panelboard.
PostPosted: Tue Aug 05, 2025 5:02 am
If I needed to series-rate a panelboard. Do I enter the rating of the breaker in the Series rating box under the component subview? I know in EasyPower I would select a check mark and it would pass on the device evaluation because it is still showing up as a fail on skm. Am I missing a step?
 Post subject: Re: Series Rating a Panelboard.
PostPosted: Tue Aug 05, 2025 8:08 am
Yes, but what about the device evaluation? is there a way to show it as passed because it is being series rated?
PostPosted: Tue Aug 05, 2025 10:42 am
Mike is correct.
If you enter a series rating in the Component Editor for the device, or bus, and that rating is higher than the X/R adjusted, calculated available fault current, it will pass the Device Evaluation.
