wbd wrote:
I would say that the method would depend on the system configuration and where you are trying to reduce the IE. In some cases it may be as simple as changing a Class RK5 fuse to a A6D Class RK1 fuse. In other cases it may require installation of an arc flash relay system.
I don't think there is one global answer and there may be several ways to reduce the IE for a particular system configuration.
Let us go one step further, both Mersen (A6D-R) and Buss (LPS-R) have two styles of Class RK1 fuses. Class R takes you through 600 amperes and 600 volts. The A6D-R and LPS-R have some intentional time-delay, that can be a problem at low fault currents. in general, either of these fuses will get you below 1.2 cal/sq cm incident energy (IE) if the fuse size does not exceed 200 amperes. If the fault current is high, they can can be used through 400 amperes to reduce the IE.
For IE reduction it is far better to use the Mersen A6K-R or the Buss KTS-R all the way through 600 amperes. In most cases you will get below 1.2 cal/sq cm, even at 600 amperes. The only limitation is you cannot use these fuses on a single across-the-line start motor or a transformer primary. On the other hand they do an excellent job feeding a bus duct or MCC. If your plug plugs or fuseible switchboard feeders are 600 amperes or less you typically can get all the process control panels under 1.2 cal/sq cm.
Over 600 Amperes and 600 Volts:Another technique is to insert the the Mersen A50QS fuse in the circuit upstream of the equipment to be protected. This works very well in front of a large drive cabinet. The problem is, finding a switch that accepts this style of fuse. Boltswitch Company makes fuse adapters all the way through 1200 amperes that fit their switches. I have been involved in multiple installations when 400A-1200A drive cabinets have the IE reduced to less than 1.2 cal/sq cm with this technique.
Drive Isolation Transformers (DIT):When you add a DIT in front of the drive cabinet you are typically increasing the IE by more than four times, that is conservative. The above technique works very well on the secondary of the DIT.