It is currently Mon Nov 23, 2026 9:27 am
 Post subject: Switchgear Viewing Windows
PostPosted: Tue May 17, 2011 4:37 pm
Operators in one of our facilities want approval to install viewing windows on 13.8kV switchgear doors to view breaker status (open, closed, test position, etc.).
These are a retrofit product from Fluke that have voltage, temperature and pull-out ratings that exceed IEEE C37.20.2 standards for viewing windows.
Is this a reasonably safe thing to do with respect to arc flash?
Regards
PostPosted: Wed May 18, 2011 4:21 am
Since the consensus is that credit is not taken for switchgear, MCC, switch doors for reducing AFH, unless specifically designed and rated as arc resistant, I don't think installing the windows will affect the choice of PPE.