It is currently Thu Oct 01, 2026 5:06 am



Post new topic Reply to topic
Author Message
 Post subject: 4160 and 13.8kV Voltage Testing
PostPosted: Fri Sep 25, 2009 1:39 pm 
User avatar

Joined: Thu Sep 24, 2009 5:46 pm
Posts: 25
The question comes up: What is acceptable for voltage testing for medium voltage? Is a Salisbury 4555 non contact tester correct? It measures electric field and will not check phase to phase and phase to ground. Should we be using the hotstick type by Megger?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Sep 25, 2009 2:36 pm 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
I don't think there is a real answer to this, I have always established the policy of non-contact check (Check the tester on a live source before and after), and if work will be done on the cables or bus then a direct contact check is also required.

We have also always used the double visual break rule (Utulities use this) for MV work and of course if it isn't grounded it isn't dead.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Sep 25, 2009 4:31 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
And use a "shotgun" stick for the grounding process.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Sep 26, 2009 2:38 pm 
User avatar

Joined: Thu Sep 24, 2009 5:46 pm
Posts: 25
Direct Contact

Zog,

What do you use for direct contact?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Sep 26, 2009 9:50 pm 

Joined: Thu Nov 15, 2007 7:58 am
Posts: 33
Location: NY
Checking dead

Get and use the AB Chance multi range detector. It comes with a self test device and is designed to be used with a hot stick. Select the stick for the voltage you are dealing with . Don't forget it is an induction device and won't read any DC static voltage that may be present . You must still apply grounds from the proper distance, or discharge the equipment before making bare-hand contact.


Attachments:
left hand rule1.JPG
left hand rule1.JPG [ 43.04 KiB | Viewed 4003 times ]
_1119162201_001.jpg
_1119162201_001.jpg [ 36.32 KiB | Viewed 4003 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Sep 27, 2009 12:30 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
alf wrote:
Zog,

What do you use for direct contact?


Biddel detex and the pizotest tester to verify the meter works before and after each test.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883