| Author: | alf [ Fri Sep 25, 2009 1:39 pm ] |
| Post subject: | 4160 and 13.8kV Voltage Testing |
The question comes up: What is acceptable for voltage testing for medium voltage? Is a Salisbury 4555 non contact tester correct? It measures electric field and will not check phase to phase and phase to ground. Should we be using the hotstick type by Megger? |
|
| Author: | Zog [ Fri Sep 25, 2009 2:36 pm ] |
| Post subject: | |
I don't think there is a real answer to this, I have always established the policy of non-contact check (Check the tester on a live source before and after), and if work will be done on the cables or bus then a direct contact check is also required. We have also always used the double visual break rule (Utulities use this) for MV work and of course if it isn't grounded it isn't dead. |
|
| Author: | acobb [ Fri Sep 25, 2009 4:31 pm ] |
| Post subject: | |
And use a "shotgun" stick for the grounding process. |
|
| Author: | alf [ Sat Sep 26, 2009 2:38 pm ] |
| Post subject: | |
Direct Contact Zog, What do you use for direct contact? |
|
| Author: | Zog [ Sun Sep 27, 2009 12:30 am ] |
| Post subject: | |
alf wrote: Zog,
What do you use for direct contact? Biddel detex and the pizotest tester to verify the meter works before and after each test. |
|