| Author: | mnewman [ Sun Jan 22, 2012 6:10 pm ] |
| Post subject: | Parallel Fuses - Equivalent Time-Current Curve |
When an arcing fault occurs downstream from two 100A fuses in parallel, can the fuses modelled by a single 100A fuse by shifting the current axis to the right by a factor of two to represent the time-current curve for the two parallel 100A fuses ? The above assumes that the current divides equally between the two 100A parallel fuses. |
|
| Author: | jvrielink [ Mon Jan 23, 2012 10:59 am ] |
| Post subject: | |
Yes you can do this, as long as your assumption holds (no difference in cable lengths, same source, etc.). I don't know which software you use, but properly modeled it may already account for the division. The arcing fault is calculated at a bus so it's not immediately obvious that the time is determined with half of it. When plotting the TCC a 2x multiplier for a single curve will help visualize the device's actual response to an arcing fault. This also makes it easy to visually check if your calculation is correct. |
|