I agree with JDB to use the "slowest" fuse, but this should be applied within the range of arcing fault currents present.
Two fuse types, even if they have different current ratings, may have some overlap. One fuse may be faster in the higher current ranges, and slower in the overload region.
Hopefully you will be performing another analysis which reflects replacement of all their fuses!
The mismatched fuses were probably installed after the originals blew. Fuses should be replaced in sets. The fault that blew the originals may have fatigued the elements of the remaining fuses enough to negatively affect their performance.