glenr4 wrote:
Hi,
I am interested in finding out, if other users apply any sort of factor to reducing incident energy when the door is closed, on a non-type tested switchboard ie not arc fault contained? A client of mine has done this in their own internal document and referenced "the NFPA tables reflect that some protection is afforded by the metal switchboard enclosure given that it sits between the arc fault and the operator."
I don't have a copy of the NFPA document (I only work on LV equipment) and don't have a contact in the client's organisation that can answer this either.
What do you think? Can it be justified?
Thanks!
See "Report on Enclosure Internal Arcing Tests", Heberlein, Higgins, and Epperly, IEEE IAS Magazine, May/June 1996, pp. 35-42, among others. CIGRE also did a lot of research on modelling for the purposes of developing arc resistant gear but the upshot is that on non-venting gear, the pressure in every test they did blew the enclosure doors off within 1 cycle. Furthermore there does not appear to be any sort of cal/cm^2 or kVA rating below which this does NOT occur. It doesn't happen every time but so far a definitive calculation has been elusive.
Doors open/doors closed is only applicable in so much as it is a convoluted way to say that the worker is outside of the restricted boundary and thus unlikely to cause an arc. Once we have an arc IF the doors stay on then the incident energy is in all likelihood never going to get above 1.2 cal/cm^2 since it is thermal radiation. That is the magic of arc resistant gear. But once the doors are off, whether they are open at the time or they are blown off, there is no difference in terms of incident energy.