It is currently Sat Nov 14, 2026 6:35 pm
 Post subject: Standby Diesel Generator
PostPosted: Tue Jan 09, 2018 11:02 am
I have to model a standby generator 200 KW and was given a fault current value from the manufacturer of around 7.6 kA. Can I just model a grid with this kA value and simulate the arc flash situation on emergency power? I am using ETAP.
Thanks!
 Post subject: Re: Standby Diesel Generator
PostPosted: Sat Jan 13, 2018 7:28 am
Thanks!
For short circuit purposes, yes. Otherwise there are reasonable approximate values for the primary and secondary (X' and X'') that can be used for arc flash calculations where ETAP uses piecewise modelling to account for the long asymmetrical fault currents. This is always a tricky situation because the available fault current is usually about an order of magnitude less than utility fault current which greatly increases the overcurrent trip times and makes incident energy values much higher than during normal operation.
PostPosted: Fri Mar 09, 2018 10:47 pm
Standby diesel generator 200KW 250KVA, the rated current should be 360 (A). To ensure safety, please consult technician at this website:
Life is an attitude.
deleted link to commercial website
PostPosted: Sat Mar 10, 2018 6:27 am
Yes but the OP was asking about modeling for short circuit and not looking for FLA