I am doing an arc flash calculations using SKM for a UV facility (2MW service) that has 480 volts UV reactors.

So when I talked to the electrician he asked me if I was going to do the calculations for the reactor panels and he told me that he needed to access those panels in order to calibrate the UV lamps. He said that the manufacturer install a second inside door where the UV reactors are behind these doors and the reactors are 2000 volts AC. When I saw the panel I realized that there is an electronic board and he needed to adjust some potentiometers using a small screw driver.

So, the service is 3 phase 480 volts, but once inside the cabinet there are 9 of these UV reactors that are 480/2000 volts single phase reactors with 50 Amps fuses on each reactor on the 480 volts side.

I do not have the UV reactor impedances. I will need to request it to the manufacturer, but the issue is that is single phase. So are the calculations accurate enough for this situation?


Attachments:
File comment: the reactor is behind this panel.
IMG_0914.JPG
IMG_0914.JPG [ 3.48 MiB | Viewed 457647 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: UV Reactors panel
PostPosted: Tue Apr 09, 2019 10:20 am 

Joined: Tue Feb 03, 2015 10:21 am
Posts: 3
I found out that the reactor is a 480 volts AC input, 15 kV AC output, rated 20 kW, single phase. I do not have the impedance value.

There is no where in the drawing that says 15 kV DC and it is using a #14 wire for the 15 kV.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883