| Arc Flash Forum https://brainfiller.com/arcflashforum/ |
|
| Bolted Pressure Switch https://brainfiller.com/arcflashforum/viewtopic.php?f=23&t=6402 |
Page 1 of 1 |
| Author: | arcflashprimero [ Mon Feb 16, 2026 11:23 am ] |
| Post subject: | Bolted Pressure Switch |
any tips on modeling an Eaton bolted pressure switch? switchboard is using a BPS as the main device with ARMS mode. would this be modeled just as a fuse? |
|
| Page 1 of 1 | All times are UTC - 7 hours |
| Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group http://www.phpbb.com/ |
|