See the attached pic.

What PPE CAT and IE level should I label the 208/120 Panel?

Thanks


Attachments:
fail sccr.jpg
fail sccr.jpg [ 22.24 KiB | Viewed 10878 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Nov 05, 2009 10:24 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
PAult wrote:
See the attached pic.

What PPE CAT and IE level should I label the 208/120 Panel?

Thanks


Well, what the study says, HRC 3. However, I would question these results, do you know all the info used for the calulation?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Nov 05, 2009 10:38 am 
Sparks Level
User avatar

Joined: Sun Aug 16, 2009 8:42 am
Posts: 184
Location: Lawrenceburg KY
This is what my label would look like. This would be for three phase not single phase.
My calculations does not include your upstream utility data. :)


Attachments:
Picture8.jpg
Picture8.jpg [ 48.07 KiB | Viewed 10877 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Nov 05, 2009 2:13 pm 

Joined: Wed Oct 29, 2008 6:05 am
Posts: 40
Zog wrote:
Well, what the study says, HRC 3. However, I would question these results, do you know all the info used for the calulation?


See the attached for more detail, using IEEE 1584 study in SKM. Basically at the max clearing time of 2.0 Seconds.

Since this Xfmr is <125 KVA and it is 208V would you label it any different?

Thanks


Attachments:
CT CORONA.jpg
CT CORONA.jpg [ 49.1 KiB | Viewed 10859 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Nov 05, 2009 2:20 pm 

Joined: Wed Oct 29, 2008 6:05 am
Posts: 40
THE CABLE GUY wrote:
This is what my label would look like. This would be for three phase not single phase.
My calculations does not include your upstream utility data. :)


I like the label.. Looks like this is generated from easypower? Do you do a study on all your transformers <125KVA? why 2* rather than 3? Did easy power calc this?

Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Nov 06, 2009 10:47 am 

Joined: Wed Oct 29, 2008 6:05 am
Posts: 40
With all the <=125KVA transformer and 208VAC arc substaining issues I think I will just use the 70E table for this application and label it with HRC 1 and an 4ft AFB.

What does everyone think?

Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Nov 06, 2009 1:17 pm 
Sparks Level

Joined: Thu Jul 19, 2007 7:54 am
Posts: 201
Location: St. Louis, MO
PAult wrote:
With all the <=125KVA transformer and 208VAC arc substaining issues I think I will just use the 70E table for this application and label it with HRC 1 and an 4ft AFB.


Well, I'm one who HATES using the Hazard/Risk Categories and 70E tables.

I haven't had to do this yet, so who knows what the final product would be, but since the transformer is only 75kVA, I would avoid putting a calorie rating on the label if I could, but would include a minimum PPE as all natural fiber, long sleeve shirt and pants, hard hat, face shield, and gloves.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Nov 06, 2009 1:19 pm 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
Exception No. 1 to 130.3 indicates that an arc flash hazard analysis is not required for 208V panels served by single transformers less than 125 kVA. IEEE Std 1584 states that

"The arc-flash hazard need only be considered for large 208 V systems: systems fed by transformers smaller than 125 kVA should not be a concern."

The clear implication is that an arc flash hazard does not exist and that because the arc will not self-sustain, the IE will be less than 1.2 cal/cm². I believe that labelling to require Category 0 PPE, 1.2 cal/cm² PPE, or even not labelling would be acceptable to meet NFPE 70E requirements. The NFPE 70E handbook for 130.3(C) states that

"Only the equipment where the incident energy level is greater than 1.2 cal/cm² needs to be marked, but that decision depends on a facility's safety program."


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Nov 10, 2009 7:14 am 

Joined: Wed Oct 29, 2008 6:05 am
Posts: 40
jghrist wrote:
"Only the equipment where the incident energy level is greater than 1.2 cal/cm² needs to be marked, but that decision depends on a facility's safety program."


I thought everything that may require service while live needed to be labeled?? I cannot find anything in 70E where it says only greater than 1.2 cal/cm2 needs to be labeled, what section is this in?

Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Nov 11, 2009 7:37 pm 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
Before that quote, I wrote
Quote:
The NFPE 70E handbook for 130.3(C) states that

This is in the handbook and not in the NFPA 70E text, so it is not governing, but the requirements for arc flash hazard labelling are all for locations where there is a potential arc flash hazard as defined in Article 100.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Nov 12, 2009 1:52 pm 
Sparks Level
User avatar

Joined: Sun Aug 16, 2009 8:42 am
Posts: 184
Location: Lawrenceburg KY
I would suggest a label at least to include HRC0 because you do not want to forget about the shock hazard and associated hazard boundaries.

I also recommend that the "Fed from" information is posted on the label to let the customer or worker easily ID the upstream protective device.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Nov 16, 2009 12:58 pm 

Joined: Wed Oct 29, 2008 6:05 am
Posts: 40
jghrist wrote:
Before that quote, I wrote

This is in the handbook and not in the NFPA 70E text, so it is not governing, but the requirements for arc flash hazard labelling are all for locations where there is a potential arc flash hazard as defined in Article 100.



Since the NEC 110.16 requires some kind of label on the equipment we are going to put the PPE category and the minimum required PPE on the labels. If we didn't label this panels with the required PPE wouldn't we have to use the tables to determine it?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Nov 16, 2009 4:29 pm 
Sparks Level
User avatar

Joined: Sun Aug 16, 2009 8:42 am
Posts: 184
Location: Lawrenceburg KY
Quote:
If we didn't label this panels with the required PPE wouldn't we have to use the tables to determine it?

Hello PAult,
I hope we are not confusing you.
I would just set your own method and not worry about the tables.

Basically, you need a company standing statement, training and noted in your final report of how to handle the HRC for task when working on this type panelboard and referencing the NFPA 70E exception to 208vac,<125KVA.

IMO, you can make this a HRC1, HRC2 or HRC3. Just make the decision and stick with it for all situations with such criteria. It’s the best thing you can do until something more definitive is determined.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Nov 17, 2009 7:45 am 

Joined: Wed Oct 29, 2008 6:05 am
Posts: 40
THE CABLE GUY wrote:
Hello PAult,
IMO, you can make this a HRC1, HRC2 or HRC3. Just make the decision and stick with it for all situations with such criteria. It’s the best thing you can do until something more definitive is determined.


Thats what I will do.

Thanks for the Help!!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Dec 04, 2009 2:07 pm 
User avatar

Joined: Fri Jan 11, 2008 4:35 pm
Posts: 14
This looks like SKM


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jan 19, 2010 5:08 pm 
User avatar

Joined: Fri Jan 11, 2008 4:35 pm
Posts: 14
Low Arc Flash Hazards

The attached file is what I use for all panels/enclosures fed by single source transformers < 125kVA, V<=240. We label for uniformity and clarity.


Attachments:
1942 Voltage Testing by Touch.jpg
1942 Voltage Testing by Touch.jpg [ 397.77 KiB | Viewed 10827 times ]
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 16 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883