 Post subject: Transformer Coupled Heating Elements
PostPosted: Wed Nov 14, 2012 11:57 am
I am redesigning a control panel for an old rotary furnace with 2-zone heating elements. The first zone is currently coupled with a 1:1 transformer which I believe is to bring the line to ground voltage down to 277V. Zone 2, however, has a 480:240 transformer. The transformer is 1/3 the size of the zone one transformer which, I understand, is because there is about 1/3 the length of heating elements in zone 2. I am lost as to why there is 240V going to zone 2. The only idea I have gotten from anyone about this question is that it may react faster/slower than the other elements because Zone 2 is just there to maintain heat. My question is: Does anyone think I need this transformer? I would like to maintain temperature within a tenth of a percent if that affects the answer.
PostPosted: Wed Nov 14, 2012 1:37 pm
It is amazing how asking question to others seems to always help me figure the answer out on my own (well, with the help of a colleague). The transformer is due to the reduced resistance in the zone two elements. 1/3 of all the elements are in zone 2, not 1/3 as many as zone 1, therefore 1/2 as many as zone 1... In case anyone was curious.