It is currently Mon Nov 23, 2026 5:08 pm
For motors that can contribute short circuit current, do you:
Include all motors 50 hp and greater 31%  31%  [ 21 ]
Include all motors regardless of hp rating 55%  55%  [ 37 ]
Something else 13%  13%  [ 9 ]
Total votes : 67
 Post subject: Motor Contribution and Arc Flash Studies
PostPosted: Sun Jul 17, 2011 3:23 pm
When performing an Arc Flash Hazard Calculation Study, IEEE 1584 suggests including all motors 50 hp (37 kW) and larger in the model to account for motor short circuit current contribution.
  • Include all motors 50 hp and greater
  • Include all motors regardless of hp rating
  • Something else
PostPosted: Mon Jul 18, 2011 8:34 am
We include motors greater than 50HP, but we also run arc flash scenarios with no motors running.
PostPosted: Tue Jul 19, 2011 9:28 am
We typically use SKM to calculate Arc Flash values. Since SKM has the ability to calculate all motor faults, we use it; it is more conservative than only considering >50hp motors.
PostPosted: Sun Jul 24, 2011 5:58 am
Why does IEEE 1584 suggest all 50 hp motors and larger be included ? Would 2 25 hp motors add the same contribution?
