Do you use the working distances from IEEE 1584:
Yes 58%  58%  [ 28 ]
No 8%  8%  [ 4 ]
Depends on the situation 29%  29%  [ 14 ]
Something else 4%  4%  [ 2 ]
Total votes : 48
 Post subject: IEEE 1584 Working Distance
PostPosted: Sun Feb 21, 2016 12:29 pm
A variation of this week's question was asked many years ago but study methods continue to evolve. IEEE 1584 - 2002 provides a table for suggested working distance to be used for the incident energy calculations. The distances are:
18 inches - Low Voltage MCCs and Panels
24 inches - Low Voltage Switchgear
36 inches - 5 kV and 15 kV Switchgear
Here is this week's question
Yes
No
Something else
Feel free to give us your thoughts about the working distance.