| Author |
Message |
arcflashprimero
Post subject: Relay modeling Posted: Mon Jan 26, 2026 11:24 am |
Do you model anything other than 50/51 settings for relays?
| Top |
bbaumer
Post subject: Re: Relay modeling Posted: Tue Jan 27, 2026 4:24 am |
| Arc Level |
Joined: Fri Jul 08, 2016 10:01 am Posts: 492 Location: Indiana
The CT ratio, curve type, any time delays or definite time setting and the breaker clearing time.
_________________ SKM jockey for hire PE in 17 states
| Top |
arcflashprimero
Post subject: Re: Relay modeling Posted: Tue Jan 27, 2026 6:13 am |
Thanks! What about upstream transformer differential protection and generator protection. Will these affect the arc flash calculations?
| Top |
bbaumer
Post subject: Re: Relay modeling Posted: Tue Jan 27, 2026 7:12 am |
| Arc Level |
Just depends on what the settings are and what breaker or breakers they are controlling and what other protection downstream busses have or don't have. I do model them and include the settings for record if nothing else but it is possible that they will affect IE, again, just depends on the setup.
| Top |