| Author: | wbd [ Thu Oct 02, 2014 4:18 am ] |
| Post subject: | Arc Rated Hood Required greated than 12 cal/cm^2 |
NFPA 70E Article 130.7(C)(10)(2) states that an arc rated hood shall be used when the anticipated incident energy exposure exceeds 12 cal/cm^2. Recently I saw a face shield that was rated for 20 cal/cm^2 and a balaclava with a 27 cal/cm^2 rating. At first glance it would appear that this combination along with safety glasses and hearing protection would be suitable head PPE for up to 20 cal/cm^2 were it not for the NFPA 70E shall statement. So I wonder why manufacturer's are offering this high cal/cm^2 rating when a face shield and balaclava cannot be used above 12 cal/cm^2? Of course one can always exceed the required ratings for added protection. Thoughts? |
|
| Author: | Voltrael [ Thu Oct 02, 2014 6:12 am ] |
| Post subject: | Re: Arc Rated Hood Required greated than 12 cal/cm^2 |
wbd wrote: NFPA 70E Article 130.7(C)(10)(2) states that an arc rated hood shall be used when the anticipated incident energy exposure exceeds 12 cal/cm^2. Recently I saw a face shield that was rated for 20 cal/cm^2 and a balaclava with a 27 cal/cm^2 rating. At first glance it would appear that this combination along with safety glasses and hearing protection would be suitable head PPE for up to 20 cal/cm^2 were it not for the NFPA 70E shall statement. So I wonder why manufacturer's are offering this high cal/cm^2 rating when a face shield and balaclava cannot be used above 12 cal/cm^2? Of course one can always exceed the required ratings for added protection. Thoughts? Seems to me that the 70E requirement is already outdated. |
|
| Author: | Leonard [ Mon Oct 06, 2014 7:30 am ] |
| Post subject: | Re: Arc Rated Hood Required greated than 12 cal/cm^2 |
Hi wbd, I cannot speak for the balaclava, however be careful with the faceshield. Someone up here in Canada has been distributing a hardhat faceshield combination with a 20 cal/cm2 rating. I have not been able to pinpoint who exactly it is. However the faceshield is heavily tinted, almost like a welding shield, no ASTM approval markings and the faceshield basically attaches to the hardhat via a heavy elastic band if you can believe it. Sounds similar to the product you are seeing Hope that this helps Best regards Len Cicero |
|
| Author: | wbd [ Mon Oct 06, 2014 4:46 pm ] |
| Post subject: | Re: Arc Rated Hood Required greated than 12 cal/cm^2 |
The 20 cal/cm^2 arc shield I saw was attached to the hardhat and would slide up underneath the hardhat. It was a green tint similar to the 12 cal/cm^2 shields I am familiar with. I believe it is of Italian manufacture. |
|