 Post subject: Rounding issues in Table 130.4(E)(a) of 70E-2024
PostPosted: Tue Sep 26, 2023 2:16 am 

Joined: Tue May 22, 2012 12:08 am
Posts: 30
I'm a little confused about the rounding applied in Column 3 (Limited Approach Boundary - Exposed Fixed Circuit Part) of Table 130.4(E)(a) in 70E-2024, especially in the light of Column 2 metric values being corrected (i.e. rounded up) from 3.0 m to 3.1 m for an imperial value of 10 ft 0 in. in the latest edition.

In particular, I'm referring to the values for the voltages ranging from 50 V to 5 kV, which are all given as 1.0 m (3 ft 6 in.).

Attachment:
NFPA_70E_2024_Table_130.4_E_a.png
NFPA_70E_2024_Table_130.4_E_a.png [ 355.16 KiB | Viewed 121501 times ]

If I convert 1.0 metre to its imperial equivalent I get approximately 3 ft 3 in.
If I convert 3 ft 6 in. to its metric equivalent I get 1.0668 m, which rounded to 1 d.p. would be 1.1 m.

I have traced the value back to NEC Table 110.26(A)(1) using the references given in Annex C.2 of 70E-2024, but am curious as to whether the metric or the imperial value is the original value?
Attachment:
NFPA_70E_2024_AnnexC_C.2.1.3.png
NFPA_70E_2024_AnnexC_C.2.1.3.png [ 123.57 KiB | Viewed 121501 times ]

Attachment:
NFPA_70_2023_NEC_Table_110.26_A_1.png
NFPA_70_2023_NEC_Table_110.26_A_1.png [ 65.99 KiB | Viewed 121501 times ]


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 1 post ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883