 Post subject: DC Arc Flash - 120V DC - Table V.3
PostPosted: Fri Aug 28, 2026 1:43 pm 

Joined: Fri Aug 28, 2026 12:36 pm
Posts: 1
I'm looking to clarify the appropriate actions for determining the arc flash risk of a UPS battery bank operating at 120VDC (industrial application).

Table V.3 indicates that the applicable voltage for consideration of the table method is a minimum of 150VDC. However, Figure F.3 indicates that 100V is the cut-off where an arc flash analysis may occur. Is there risk at 120V?

This link provided useful guidance, but I'm looking to understand how Z462 interprets the risk and ultimately some guidance that can be used for our facility maintenance personnel.


viewtopic.php?f=7&t=5708&p=25242&hilit=dc+arc+flash#p25242


Attachments:
File comment: Example of facility battery bank
UPS-9402 BATTERY BANK.jpg
UPS-9402 BATTERY BANK.jpg [ 9.6 MiB | Viewed 85398 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: DC Arc Flash - 120V DC - Table V.3
PostPosted: Wed Nov 04, 2026 7:48 am 
Sparks Level

Joined: Sun Sep 23, 2007 5:00 pm
Posts: 152
Location: Calgary, Alberta, Canada
Rusty the original arcing fault sustainabilty voltage was 100VDC. Independant research completed and we updated Table V.3 ≥150V dc. I recommend 8.0 to 12.0 cal/cm2 ATPV for 125VDC UPS battery or distribution panel work tasks. Employers Electrical Safety Program documents this.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883