It is currently Fri Aug 07, 2026 11:59 am
 Post subject: Utility source impedance
PostPosted: Sat Oct 04, 2014 10:52 am
The utility company has provided me with the actual fault current on the secondary side of the Utility transformer but no source impedance information. Would the source impedance be applicable on the secondary side of the utility transformer?
 Post subject: Re: Utility source impedance
PostPosted: Sat Oct 04, 2014 12:31 pm
The source impedance on the secondary side of the transformer would include the transformer impedance.
PostPosted: Sat Oct 04, 2014 2:33 pm
What is the transformer nameplate KVA rating, %Z and X/R ratio, and how big is the fault current value provided by the utility company on secondary of the transformer?
PostPosted: Sun Oct 05, 2014 11:26 am
2500 kVA at 5.7%Z (X/R unknown), 45kA fault current.
PostPosted: Sun Oct 05, 2014 12:44 pm
What is the transformer secondary voltage?
PostPosted: Sun Oct 05, 2014 5:27 pm
480V. (Transformer is 24kV to 480V)
PostPosted: Sun Oct 05, 2014 7:31 pm
The source impedance, avail short circuit current and short circuit MVA on primary side of the 2500KVA, 5.7%Z 24KV/480V rated transformer with 45KA avail short circuit current on its secondary is roughly equal to 2Ohms, 6kA and 250MVA respectively.
