| Author |
Message |
dorelvigu@gmail.com
Post subject: LV SWG Arc Flash calculation (with panelboards) Posted: Thu May 16, 2019 4:38 am |
Hello
For Arc Flash calculation in ETAP I asigned it as SWG and calculate the incident energy for 24in working distance. However I received comments that the working distance should be 18in.
We are working in a team of two. My colleague with is my supervisor in this project, consider we have just to reduce the working distance to 18in. We obtain 51cal/cm2.
| Top |
wilhendrix
Post subject: Re: LV SWG Arc Flash calculation (with panelboards) Posted: Mon May 20, 2019 8:25 am |
There are many unknowns in your description. Is this a switchgear or switchboard? You say SWG, which I assume means switchgear, but you also mention 30 amps fuses and a panelboard.
| Top |
Leonard
Post subject: Re: LV SWG Arc Flash calculation (with panelboards) Posted: Mon May 20, 2019 8:33 am |
| Top |
dorelvigu@gmail.com
Post subject: Re: LV SWG Arc Flash calculation (with panelboards) Posted: Tue May 21, 2019 11:07 am |
I uploaded the SWG nameplate
| Attachments: |
File comment: swg nameplate
| Top |
dorelvigu@gmail.com
Post subject: Re: LV SWG Arc Flash calculation (with panelboards) Posted: Tue May 21, 2019 11:08 am |
| Attachments: |
| Top |
dorelvigu@gmail.com
Post subject: Re: LV SWG Arc Flash calculation (with panelboards) Posted: Tue May 21, 2019 11:13 am |
SWG front and side view
| Attachments: |
| Top |
JBD
Post subject: Re: LV SWG Arc Flash calculation (with panelboards) Posted: Wed May 22, 2019 6:32 am |
Joined: Mon Jan 18, 2010 11:35 am Posts: 619 Location: Wisconsin
| Top |
dorelvigu@gmail.com
Post subject: Re: LV SWG Arc Flash calculation (with panelboards) Posted: Wed May 22, 2019 9:40 am |
Now I have the Siemens confirmation, the equipment is a Switchboard. I found in ETAP a tool, is a manual setting calculator for arc flash energy, really nice tool.
| Top |
fastmvr
Post subject: Re: LV SWG Arc Flash calculation (with panelboards) Posted: Mon Jun 03, 2019 7:21 am |
Joined: Thu Jan 25, 2018 7:13 am Posts: 2 Location: DFW Area TX
| Top |
wilhendrix
Post subject: Re: LV SWG Arc Flash calculation (with panelboards) Posted: Mon Jun 03, 2019 8:28 am |
[/size]
| Top |
[ 10 posts ] |