This is the first time to deal with three winding Transformer in SKM.
I have a three Winding transformer with 1.5MW Secondary and 0.5 MW Tertiary. I had to modify the Tertiary side of the transformer by adding more load and CBs into it. Now the Tertiary side has less incident energy. which is good.
However, the secondary side, even though I haven't change anything, has be affected. The arc Flash incident energy has jumped from 6.0 Cal/cm^2 to almost 80Cal/cm^2. Could that be possible?

Noting it's a huge transformer so for the incident energy to reach 80 cal/cm @ 2Sec is possible.


Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Three winding Transformer and Incident energy
PostPosted: Wed Feb 21, 2024 6:51 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 497
Not enough information to answer as I'd have to see the protection scheme but my question is, what type of transformer is this and what are the voltages? Are you actually labeling it? What are you using for box size or is this a substation transformer with terminations in open air? What are you using for bus gaps?

I seen others blindly model transformers with the default "PNL" or "SWG" VCB without accounting for the actual enclosure size or bus gaps or if it is in the air and not a box etc. and the results are not reality.

Voltage may also be an issue and SKM might not be the right tool, or it may be.

Again, not enough information.

Also, need to make sure you have the transformer data completely input accurately.

https://www.skm.com/applicationguides5.html

Attachment:
3windingskmhelp.jpg
3windingskmhelp.jpg [ 186.7 KiB | Viewed 42548 times ]

_________________
95% Retired


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883