It is currently Sun Nov 08, 2026 8:48 pm
 Post subject: Relay modeling
PostPosted: Mon Jan 26, 2026 11:24 am
Do you model anything other than 50/51 settings for relays?
 Post subject: Re: Relay modeling
PostPosted: Tue Jan 27, 2026 4:24 am
The CT ratio, curve type, any time delays or definite time setting and the breaker clearing time.
PostPosted: Tue Jan 27, 2026 6:13 am
Thanks! What about upstream transformer differential protection and generator protection. Will these affect the arc flash calculations?
PostPosted: Tue Jan 27, 2026 7:12 am
Just depends on what the settings are and what breaker or breakers they are controlling and what other protection downstream busses have or don't have. I do model them and include the settings for record if nothing else but it is possible that they will affect IE, again, just depends on the setup.