Our local Utility providers often respond to requests for info with design letters that indicate the upstream transformer(s) and conductor sizes, lengths, and number per phase, along with their calculated AFC at the point of demarcation (usually listed as the meterbase).

Here's the thing: No matter what I do, I can never get anywhere close to that AFC value using the information they've given. Typical Utility-provided AFC values range from about 20-32kA for a standard commercial facility. However, even when I assume infinite bus, when I add the Service transformer and incoming cables to the mix, it often drops the AFC at the same point of demarcation down to less than 10kA.

Any idea why this might be? And I know this is similar to other questions I've asked before, but am I better off using their AFC, or modeling the equipment they have? Any idea how I could replicate their numbers while still modeling the equipment they've disclosed?

I've provided an example below. When I model the equipment indicated in the picture, even when assuming an infinite bus, it kicks the AFC at point of demarcation down to 5.91kA. No matter what value I set for the Utility MVA and X/R ratios, their shown transformer chokes the AFC to the secondary and beyond down to about 6.4kA.


Attachments:
DESIGN EXAMPLE.jpg
DESIGN EXAMPLE.jpg [ 215.48 KiB | Viewed 31462 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Repeating Utility's projected AFC at meterbase
PostPosted: Thu May 28, 2026 1:26 pm 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 78
Okay, I'm an idiot. I forgot they make their AFC calcs based on their 'worst-case' transformer, shown on the left. Modeling that transformer puts me at around the AFC they show. Time to go back to school.... :?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883