If I have a 300 kVA utility transformer bank made up of 3 single phase 100 kVA transformers each with an impedance of 1.9%, is the equivalent impedance of the 300 kVA transformer simply 3 x 1.9, or is it the square root of 3 times 1.9?
PostPosted: Thu Jul 29, 2010 9:51 am
1.9%. The impedance is a per phase value.
PostPosted: Fri Jul 30, 2010 8:04 am
How are the transformers connected? Wye or delta?
PostPosted: Sat Jul 31, 2010 10:42 am
Connected delta-wye.
PostPosted: Mon Aug 02, 2010 8:52 am
Edited: Sorry I misremembered. Connections make no difference. 1.9% using 100 kVA and line to neutral voltage to get ohms secondary equates to 1.9% using 300 kVA and line to line voltage.
PostPosted: Tue Aug 03, 2010 6:38 am
No matter how the 3 single phase transformer connected, the impedance should be the same as the single phase tested value
PostPosted: Tue Jun 07, 2011 12:32 pm
What is one of the transformers has a different nameplate impedance?
PostPosted: Fri Jun 10, 2011 8:35 am
Then there is no equivalent three phase impedance.
PostPosted: Sun Jun 12, 2011 6:08 pm
Can 3 single phase transformers with different IZ% be connected to a transformer bank?
PostPosted: Sun Jun 12, 2011 10:33 pm