brainfiller wrote:
IEEE 1584 has an exception
Equipment below 240 V need not be considered unless it involves at least one 125 kVA or larger low impedance transformer in its immediate power supply. This is interpreted as no arc flash calculations are necessary and assumes the incident energy would not be as significant (although an arc flash hazard still exists)
IEEE 1584 is presently under revision. New language may replace the 125 kVA cut off with a value of short circuit current.
Do you think overall, a short circuit cut off would be easier to use than a transformer kVA cut off?
No Arc Flash is more related to Joules, it is the magnitude of the energy not just the current, and the magnitude of energy is better expressed in the form of kVA.
Yes an ARC flash exists but at the lower voltage the cal/cm2 is not making it below 125 kVA unless you get into prolonged periods of time of the arc event.
An overall short circuit cutoff would be good only if one voltage is factored, they are trying to account for all circuits below 240. Also they are considering the transformer impedance into the equation. I would say the biggest problem at the lower voltage and the lower kVA is to do with the clearing time of the protection device. At the lower capacity it may not immediately trip or in the case of a fuse melt, and prolong the time the short circuit exists.